For a continuously loaded appliance rated at 30 amperes, what is the minimum branch circuit rating required if the circuit device is not listed for continuous loading?

Prepare for the PSI Journeyman Exam with quizzes designed for success. Utilize flashcards, multiple choice questions, hints, and explanations to ensure you’re ready for the test day!

To determine the minimum branch circuit rating required for a continuously loaded appliance rated at 30 amperes, it’s important to recognize the National Electrical Code (NEC) guidelines regarding continuous loads. A continuous load is defined as a load where the maximum current is expected to continue for three hours or more.

According to the NEC, for continuous loads, the circuit conductors and the branch circuit protective device must be rated at 125% of the continuous load to ensure that the circuit operates safely over time without tripping.

In this case, the appliance is rated at 30 amperes. To find the required circuit rating, you multiply the load by 125%:

30 amperes × 1.25 = 37.5 amperes.

The branch circuit rating must be selected as a standard rating that is above 37.5 amperes. Since the options provided are whole numbers, the closest and appropriate minimum that meets or exceeds this requirement is 40 amperes. Therefore, a branch circuit rated at 40 amperes can safely handle the continuous load without the risk of overheating or causing a nuisance tripping of the circuit breaker.

The higher ratings, such as 50 amperes and 60 amperes, exceed the requirement but